Manual operation stopped working

Jeff Davidson
Actualizado 2022-08-07 22:23:56 UTC
Tema: Hogar conectado

Manual operation of zones used to work, but not longer does. Sprinklers operate as desired although when I select manual operation/play, they say they are on, although never turn on, please help resolve this. 

Ver: 2250    Seguir: 0   

1 Respuesta    Haga clic en la respuesta para ver la respuesta completa y los comentarios.


Wency Pan
Actualizado 2022-08-08 06:16:58 UTC

Dear customer,


Please check the wires. Are they loose or disconnected from the slots? Please also check the common wires and the master valve if you have one. If you believe the wires are correctly installed,  please check if there is a main valve/faucet that is turned off manually. 

To test if the controller is working properly, use a multimeter (AC voltage mode) to test the voltage between the common wire and the zone wire when the zone is active. Normally the voltage should be between 24V and 28V.

You might also want to check whether there are shorted zones or open zones. You just need to use a multimeter to measure the resistance between the common wire and each zone (remove the wires from the slots before testing the resistance). The normal reading would be 20-60 Ohms. If the reading is less than 10 Ohms then you might have a shorted circuit in the solenoid and if it is larger than 80 Ohms you might have an open circuit. 

Thanks,

Wency

Netro Support